If a 3 phase, 25 kV (L-L), 50Hz Star connected synchronous generator runs at 1000 rpm. Then, the number of poles and voltage per phase is _______ & ________ respectively.Select one:a.6 poles, 15080.8 Vb.6 poles, 13334.5 Vc.12 poles, 15008 Vd.6 poles, 14433.7 V

Question

If a 3 phase, 25 kV (L-L), 50Hz Star connected synchronous generator runs at 1000 rpm. Then, the number of poles and voltage per phase is _______ & ________ respectively.Select one:a.6 poles, 15080.8 Vb.6 poles, 13334.5 Vc.12 poles, 15008 Vd.6 poles, 14433.7 V

🧐 Not the exact question you are looking for?Go ask a question

Solution

The number of poles in a synchronous generator can be calculated using the formula:

P = 120f/N

where: P = number of poles f = frequency N = speed in rpm

Substituting the given values:

P = 120*50/1000 P = 6 poles

So, the generator has 6 poles.

The line-to-line voltage (VLL) in a star connection is √3 times the phase voltage (Vph). So, we can find the phase voltage using the formula:

Vph = VLL/√3

Substituting the given line-to-line voltage (25 kV = 25000 V):

Vph = 25000/√3 Vph = 14433.7 V

So, the phase voltage is 14433.7 V.

Therefore, the correct answer is d. 6 poles, 14433.7 V.

This problem has been solved

Similar Questions

A 415-V, 50-Hz supply is applied to a three-phase star-connected balanced load. Each [10]phase has an impedance of R+jX ohms, where R=15 n and X = 13.4 n. Find the(i) phase voltage, f'2(ii) phase current,(iii) line current,(iv) power factor,(v) active power,(vi) reactive power,S,vii) total VA

A three-phase, 220 V, 50 Hz, induction motor has 6 poles. What is the synchronous speed and the rotor speed of this induction motor when the slip is 0.03?Question 3Answera.Ns = Nr = 1500 rpmb.Ns=1500 rpm and Nr=1455 rpmc.Ns=1000 rpm and Nr=970 rpmd.Ns=1500 rpm and Nr=1000 rpm

A balanced three-phase star-connected supply of phase sequence ABC feeds a balancedstar connected load of impedance 5025°Ω in each phase. Phase voltage of Phase A ismeasured to be 24030° V.a) Determine the magnitude and phase of each line current supplied by the source.b) Determine the active power and the reactive power supplied by the source.c) Determine the reactive power requirement of each of the three capacitances,connected in star, to improve the power factor to 0.95 lag.

A balanced star connected load of (2+j3) Ω per phase and a balanced delta-connected load of(6+j6) Ω per phase are connected in parallel to a three phase, 400V, 50Hz supply. Calculate thephase current in each load, the total current in each supply line, the total power supplied and theoverall power factor.

A 3-phase delta connected load consumes a power of 60kW taking a lagging current of 200 A at a line voltage of 400V, 50 Hz. Find the parameters of each phase. What would be the power consumed if the load where connected in star.