A 3-phase delta connected load consumes a power of 60kW taking a lagging current of 200 A at a line voltage of 400V, 50 Hz. Find the parameters of each phase. What would be the power consumed if the load where connected in star.

Question

A 3-phase delta connected load consumes a power of 60kW taking a lagging current of 200 A at a line voltage of 400V, 50 Hz. Find the parameters of each phase. What would be the power consumed if the load where connected in star.

🧐 Not the exact question you are looking for?Go ask a question

Solution

The given parameters are:

  • Power consumed, P = 60 kW
  • Line current, I_L = 200 A
  • Line voltage, V_L = 400 V
  • Frequency, f = 50 Hz

Step 1: Calculate the power factor (cos θ)

The power factor can be calculated using the formula P = √3 * V_L * I_L * cos θ. Rearranging for cos θ gives us:

cos θ = P / (√3 * V_L * I_L) = 60,000 / (√3 * 400 * 200) = 0.433

Step 2: Calculate the phase current (I_ph)

For a delta connection, the phase current is given by I_ph = I_L / √3 = 200 / √3 = 115.47 A

Step 3: Calculate the phase voltage (V_ph)

For a delta connection, the phase voltage is equal to the line voltage, V_ph = V_L = 400 V

Step 4: Calculate the impedance (Z)

The impedance can be calculated using Ohm's law, Z = V_ph / I_ph = 400 / 115.47 = 3.46 Ω

Step 5: Calculate the power consumed in star connection

In a star connection, the line current is equal to the phase current and the line voltage is √3 times the phase voltage. Therefore, the power consumed in a star connection can be calculated using the formula P = √3 * V_L * I_L * cos θ = √3 * 400 * 115.47 * 0.433 = 36.05 kW

So, the parameters for each phase in the delta connection are:

  • Power factor = 0.433
  • Phase current = 115.47 A
  • Phase voltage = 400 V
  • Impedance = 3.46 Ω

And the power consumed if the load were connected in star would be 36.05 kW.

This problem has been solved

Similar Questions

A balanced three phase star connected load of 18 kilo watt taking a leading current of 60 A when connected across a 3 phase 440V, 50Hz supply. Find the values and nature of the load

A balanced star connected load of (2+j3) Ω per phase and a balanced delta-connected load of(6+j6) Ω per phase are connected in parallel to a three phase, 400V, 50Hz supply. Calculate thephase current in each load, the total current in each supply line, the total power supplied and theoverall power factor.

A 415-V, 50-Hz supply is applied to a three-phase star-connected balanced load. Each [10]phase has an impedance of R+jX ohms, where R=15 n and X = 13.4 n. Find the(i) phase voltage, f'2(ii) phase current,(iii) line current,(iv) power factor,(v) active power,(vi) reactive power,S,vii) total VA

Three equal impedances are first connected in delta across a three-phase balanced supply. If the same impedances are connected in star across the same supplya.phase current will be one-thirdb.line current will be one-thirdc.noned.power consumed will be one-third

A balanced three-phase star-connected supply of phase sequence ABC feeds a balancedstar connected load of impedance 5025°Ω in each phase. Phase voltage of Phase A ismeasured to be 24030° V.a) Determine the magnitude and phase of each line current supplied by the source.b) Determine the active power and the reactive power supplied by the source.c) Determine the reactive power requirement of each of the three capacitances,connected in star, to improve the power factor to 0.95 lag.

1/3

Upgrade your grade with Knowee

Get personalized homework help. Review tough concepts in more detail, or go deeper into your topic by exploring other relevant questions.