a single-phase transformer has a turn ratio of 1:2 and is connected to a purely resistive load.the magnetizing current drawn is 1a.if core losses and leakage reactance are neglected, the primary current is-1.41a2a2.24a3a
Question
a single-phase transformer has a turn ratio of 1:2 and is connected to a purely resistive load.the magnetizing current drawn is 1a.if core losses and leakage reactance are neglected, the primary current is-1.41a2a2.24a3a
Solution
The primary current in a transformer is the sum of the magnetizing current and the load current.
Given that the transformer has a turn ratio of 1:2, this means that the voltage is stepped up by a factor of 2, and the current is stepped down by the same factor.
If the load is purely resistive, the load current on the secondary side will be in phase with the voltage.
Assuming a secondary current of 1A (since the current is stepped down by a factor of 2), the primary current will be the secondary current divided by the turn ratio, or 1A/2 = 0.5A.
Adding the magnetizing current of 1A, the total primary current is 1A + 0.5A = 1.5A.
However, the given options do not include 1.5A. This could be due to a mistake in the problem statement or the given options.
Please check the problem statement and the given options. If the problem statement and the options are correct, then the answer is not among the given options.
Similar Questions
An 10000/100V, 50 Hz, single phase transformer has an exciting current of 0.8 A and a core loss of 400 W when its HV side is energized at rated voltage. The core loss component of the existing current is ?
The no-load current drawn by the transformer is usually what percent of the full-load current ? (a) 0.2 to 0.5 per cent (b) 2 to 5 per cent (c) 12 to 15 percent (
How does the output of an inductively loaded, 1-phase transformer different with the unloadedtransformer?
Transformer cores are laminated to reduce ……*1 pointLenz’s currentFaraday’s electromagnetic inductionEddy currentsAmpere’s current
A single Phase 50kVA, 2400/240V, 60Hz distribution transformer is used as a step downtransformer at the load end of a 2400V feeder whose series impedance is (1.0 + j2.0) ohms. Theequivalent series impedance of the transformer is (1.0 + j2.5) ohms referred to the high voltage (i.e.primary) side. The transformer is delivering rated total power at 0.8 power factor lagging, and atrated secondary voltage. Neglecting the transformer excitation current, determine:(a) The voltage at the transformer primary terminals,(b) The voltage at the sending end of the feeder,(c) The real and reactive power delivered to the sending end of the feeder.Work in the Per Unit System, using the transformer ratings as base quantities