an induction motor draws 50 KW at a 0.60 lagging power factor from a 480 v, 60 Hz source. What parallel capacitor will increase the overall power factor to 0.90 lagging?

Question

an induction motor draws 50 KW at a 0.60 lagging power factor from a 480 v, 60 Hz source. What parallel capacitor will increase the overall power factor to 0.90 lagging?

🧐 Not the exact question you are looking for?Go ask a question

Solution

To solve this problem, we need to follow these steps:

  1. Calculate the apparent power (S) and reactive power (Q) before the capacitor is added.

The apparent power S (in kVA) is given by the formula: S = P/PF, where P is the real power (in kW) and PF is the power factor.

So, S = 50 kW / 0.60 = 83.33 kVA.

The reactive power Q (in kVAR) is given by the formula: Q = sqrt(S^2 - P^2), where S is the apparent power (in kVA) and P is the real power (in kW).

So, Q = sqrt((83.33 kVA)^2 - (50 kW)^2) = 66.67 kVAR.

  1. Calculate the reactive power (Q_new) after the capacitor is added.

The new apparent power S_new (in kVA) is given by the formula: S_new = P/PF_new, where P is the real power (in kW) and PF_new is the new power factor.

So, S_new = 50 kW / 0.90 = 55.56 kVA.

The new reactive power Q_new (in kVAR) is given by the formula: Q_new = sqrt(S_new^2 - P^2), where S_new is the new apparent power (in kVA) and P is the real power (in kW).

So, Q_new = sqrt((55.56 kVA)^2 - (50 kW)^2) = 25 kVAR.

  1. Calculate the reactive power (Q_c) provided by the capacitor.

The reactive power Q_c (in kVAR) provided by the capacitor is given by the formula: Q_c = Q - Q_new, where Q is the original reactive power (in kVAR) and Q_new is the new reactive power (in kVAR).

So, Q_c = 66.67 kVAR - 25 kVAR = 41.67 kVAR.

  1. Calculate the capacitance (C) of the capacitor.

The capacitance C (in F) is given by the formula: C = Q_c / (2 * pi * f * V^2), where Q_c is the reactive power provided by the capacitor (in kVAR), f is the frequency (in Hz), and V is the voltage (in V).

So, C = 41.67 kVAR / (2 * pi * 60 Hz * (480 V)^2) = 0.0000023 F or 2.3 µF.

Therefore, a parallel capacitor of 2.3 µF will increase the overall power factor to 0.90 lagging.

This problem has been solved

Similar Questions

A 208 Volt, 18 Amp synchronous motor is operating at a lagging power factor of 0.8. How many watts of power will the motor be producing?

A 3-phase, 1.5 kW, 415 V, 2-pole, 50 Hz, 2910 rpm induction motor delivers rated output power to a load. If the rotational loss is 150 W, determine the air-gap power.

10 kW, 6-pole, 50 Hz, 3- phase induction motor has linear torque-slip characteristicsbetween zero torque and maximum torque. The slip at which maximum torque of 520 Nmoccurs is 0.2. For mechanical losses of 600 W, find the speed at which motor would run whiledelivering rated shaft power

10 kW, 6-pole, 50 Hz, 3- phase induction motor has linear torque-slip characteristicsbetween zero torque and maximum torque. The slip at which maximum torque of 520 Nmoccurs is 0.2. For mechanical losses of 600 W, find the speed at which motor would run whiledelivering rated shaft power.

A 50 hp, 240 V, 4 poles, 60 Hz, Delta connected, three phase induction motor, ifR 1 =0,4 ohm, R’ 2 =0,6 ohm, X 1 =1,0 ohm, X’ 2 =1,0 ohm, n s =1800 and n=1710.Find the following quantities:a) I 1 =I’ 2 =?b) t=?c) I st =?d) t st =?e) t max =?f) S max =?g) Sketch thetorque-speedcharacteristic

1/1

Upgrade your grade with Knowee

Get personalized homework help. Review tough concepts in more detail, or go deeper into your topic by exploring other relevant questions.